5.2 METHODOLOGY FOR TECHNICAL STUDY<br />

Following captive power plants were selected jointly by CSERC and CSEB for detailed study:<br />

Sr.<br />

No.<br />

Name of selected<br />

captive power plants<br />

Table-V<br />

Total Installed<br />

Capacity in MW<br />

Total Installed<br />

Capacity in MVA<br />

C<strong>on</strong>tract demand<br />

with CSEB in MVA<br />

1 P 810<br />

993.1<br />

120<br />

2 Q 325.7<br />

364.6<br />

1<br />

3 R 20<br />

25.0<br />

1.8<br />

4 S 55<br />

68.8<br />

10<br />

5 T 21.5<br />

26.9<br />

8<br />

6 U 14.3<br />

16.0<br />

2.75<br />

7 V 15<br />

19.6<br />

6<br />

8 W 43<br />

57.8<br />

3.125<br />

9 X NA<br />

0.0<br />

16<br />

10 Y 15<br />

18.7<br />

2<br />

TOTAL 1319.5 1590.5 170.68<br />

It was jointly decided to carry out measurement at the point of comm<strong>on</strong> coupling with<br />

(a) Grid interc<strong>on</strong>necti<strong>on</strong>( <strong>parallel</strong> operating c<strong>on</strong>diti<strong>on</strong>)<br />

(b) Without grid interc<strong>on</strong>necti<strong>on</strong> (Islanding operating c<strong>on</strong>diti<strong>on</strong>)<br />

But ERDA was not granted permissi<strong>on</strong> for measurements in islanding mode as the CPPs<br />

expressed their inability to run in isolated mode. Hence, ERDA has carried out the<br />

measurements at following two locati<strong>on</strong>s as jointly decided -<br />

(1) Point of comm<strong>on</strong> coupling, and<br />

(2) Generator output terminals.<br />

ERDA has carried out measurements for 24 hours at above menti<strong>on</strong>ed locati<strong>on</strong>s for the<br />

selected CPPs. Technical report of the results of the measurements has been submitted to the<br />

Commissi<strong>on</strong>. The highlights of the study results observed from measurements and power<br />

system studies are given in clause 5.3.<br />

ERDA has also collected required data for power system studies from the transmissi<strong>on</strong> divisi<strong>on</strong><br />

of CSEB for carrying out the load flow and fault level calculati<strong>on</strong>.<br />