5.3.2 NEGATIVE PHASE SEQUENCE CURRENT<br />

Fig.3 Negative phase sequence current at point of comm<strong>on</strong> coupling<br />

Fig.4 Negative phase sequence current at generator output<br />

Fig. 3 and Fig. 4 show the variati<strong>on</strong> in the negative phase sequence current measured at point<br />

of comm<strong>on</strong> coupling (132 kV) and at generator output terminal respectively for a typical captive<br />

power plant. It is found that the magnitude of negative phase sequence current at the point of<br />

comm<strong>on</strong> coupling is much higher than that at generator output terminal. Higher negative phase<br />

sequence current at PCC clearly indicates the support drawn by CPP from grid.<br />