5.3.6 APPARENT POWER IMPORT AND EXPORT<br />

Fig.11 Apparent Power Import and Export<br />

From the fig. 11, it is clear that captive power plant can supply the excess power to the utility<br />

grid <strong>on</strong>ly after meeting the requirement for in-house loads.<br />

Above are the results of power quality parameters measured for <strong>on</strong>e typical captive power plant.<br />

In the similar way power quality parameters have been measured for 10 nos. of sample captive<br />

power plants. From these graphical representati<strong>on</strong>s, it is clear that Grid provides support<br />

through <strong>parallel</strong> operati<strong>on</strong> in terms of:<br />

Absorbing harm<strong>on</strong>ics<br />

Absorbing negative phase sequences current<br />

Improvement in power factor<br />

Meeting fluctuati<strong>on</strong>s in load<br />

Providing reactive power support, etc.<br />

5.4 FAULT LEVEL AT POINT OF COMMON COUPLING<br />

In additi<strong>on</strong> to the measurements of power quality parameters, the fault level at point of comm<strong>on</strong><br />

coupling have been obtained through system study analysis as total fault level and quantum of<br />

fault level c<strong>on</strong>tributed by CPP.<br />