5.3.6 APPARENT POWER IMPORT AND EXPORT<br />
Fig.11 Apparent Power Import and Export<br />
From the fig. 11, it is clear that captive power plant can supply the excess power to the utility<br />
grid <strong>on</strong>ly after meeting the requirement for in-house loads.<br />
Above are the results of power quality parameters measured for <strong>on</strong>e typical captive power plant.<br />
In the similar way power quality parameters have been measured for 10 nos. of sample captive<br />
power plants. From these graphical representati<strong>on</strong>s, it is clear that Grid provides support<br />
through <strong>parallel</strong> operati<strong>on</strong> in terms of:<br />
Absorbing harm<strong>on</strong>ics<br />
Absorbing negative phase sequences current<br />
Improvement in power factor<br />
Meeting fluctuati<strong>on</strong>s in load<br />
Providing reactive power support, etc.<br />
5.4 FAULT LEVEL AT POINT OF COMMON COUPLING<br />
In additi<strong>on</strong> to the measurements of power quality parameters, the fault level at point of comm<strong>on</strong><br />
coupling have been obtained through system study analysis as total fault level and quantum of<br />
fault level c<strong>on</strong>tributed by CPP.<br />